wwhitney
- Berkeley, CA
- Retired
For the 2023 NEC I submitted PI 92-NFPA 70-2019 to expand 705.12(B)(3)(3) (sum of all breakers rule), so that the sum also excludes one breaker of the smallest size present. The physics on this is clear, it's still impossible to overload the bus under normal conditions.
This would allow, for example, a solar combiner box with, say, a 60A supply, a 60A busbar, (3) 20A OCPDs for microinverter circuits, and a 15A or 20A OCPD for monitoring equipment. It would also allow, say, a 100A panel with a 100A utility supply, a 100A breaker for on site generation (PV/ESS inverters), and a 100A breaker for a load panel (and no other breakers).
The CMP's response was "Adding additional features to this very simple rule creates unnecessary confusion for the enforcement and marking requirements." That's obviously a judgement call, and if the additional allowance would not be of practical use, I would agree. On the other hand, if it is something solar designers would regularly avail themselves of to simply installations and reduce materials used, I disagree.
So I'm asking practicing solar designers and others what they think about the idea, and if it would be useful to them, to submit a public comment on the issue by the closing date of August 19, 2021. Also please comment here so I can formulate my own public comment appropriately.
Thanks,
Wayne
Thanks,
Wayne