I am not sure I understand the setup. Is the box in the center of your image a junction box, with wires coming in from the breaker being tied to wires leading out to each of the bathrooms? Also, are the GFCIs you mention in each of the three bathrooms (i.e., not the breaker itself)? Finally, what do you mean by "upstream" (i.e., no bathroom appears to be upstream of any other)?
If this is what I think it is, then I would say it is code compliant. Be advised, however, that this circuit can feed nothing in any bathroom other than receptacles, and can feed nothing outside the bathrooms.
Why use a j-box at all? Run the bath circuit to the receptacle location in each bath, pigtail it, and don't do any line-load connections. A GFCI in each bath with only the line side connected. Perfectly legal.
Why use a j-box at all? Run the bath circuit to the receptacle location in each bath, pigtail it, and don't do any line-load connections. A GFCI in each bath with only the line side connected. Perfectly legal.
sorry, if it were a one line circuit, the first GFCI tripped would cut power to everything downstream
Not if you connect the line in and line out wires to only the line terminals on each GFCI and ignore the load terminals.
In fact, this is so commonly done, they're made to accept two wires on each one, so you only need to pigtail the EGC.
Correct. A GFCI receptacle has a line and load side. When it trips, only the LOAD side terminals (and the receptacle itself) are disconnected. The line side is unaffected. So running from the line side to another bathroom is not affected by a GFCI tripping.
BTW, why is it they can't make the EGC screw/plate/etc accept two wires like the others? I wouldn't always want to do it, but it sure would be a nice option....In fact, this is so commonly done, they're made to accept two wires on each one, so you only need to pigtail the EGC.
BTW, why is it they can't make the EGC screw/plate/etc accept two wires like the others? I wouldn't always want to do it, but it sure would be a nice option.
They used to, and some receptacles had two grounding screws. Then they added the rule that ground continuity may not depend on the device terminations.
Ah, got it. Just like a neutral of a MWBC. Thanks.
Hmmm, except we can just use the device screws for grounding the device (when designed for it) itself (and whatever is plugged in) to a grounded box...