Would You Combine

Status
Not open for further replies.

Alwayslearningelec

Senior Member
Location
NJ
Occupation
Estimator
Would you run the receptacle circuit in the same conduit as the ACCU circuit? Wonder if they would allow it even if you were to run 1-1/4". I didn't look into the derating.

1708712534509.png
 
I would run my receptacle circuit along with my ACCU circuit.
 
I would use the same raceway for both. As noted check the derating first and then the fill if the conductor size changes.
 