A Alwayslearningelec Senior Member Location NJ Occupation Estimator Feb 23, 2024 #1 Would you run the receptacle circuit in the same conduit as the ACCU circuit? Wonder if they would allow it even if you were to run 1-1/4". I didn't look into the derating.
Would you run the receptacle circuit in the same conduit as the ACCU circuit? Wonder if they would allow it even if you were to run 1-1/4". I didn't look into the derating.
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Feb 23, 2024 #2 I would run my receptacle circuit along with my ACCU circuit.
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician (retired) Feb 23, 2024 #3 I would use the same raceway for both. As noted check the derating first and then the fill if the conductor size changes.
I would use the same raceway for both. As noted check the derating first and then the fill if the conductor size changes.