WP GFCI outdoor required in a comm./Indust.?

Status
Not open for further replies.

zappy

Senior Member
Location
CA.
Are gfci's required to be WP rated outdoors in commercial or industrial buildings? TY for your help.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Are you referencing type "WR" (406.9) If so, yes,

All 15- and 20-ampere, 125- and 250-volt nonlocking-type receptacles shall be listed and so identified as the weatherresistant type.
 

zappy

Senior Member
Location
CA.
Are you referencing type "WR" (406.9) If so, yes,

All 15- and 20-ampere, 125- and 250-volt nonlocking-type receptacles shall be listed and so identified as the weatherresistant type.
Yes, WR I mean. So this code isn't just for Resi.? Boss said show him in the code book.
 