hillbilly1
Senior Member
- Location
- North Georgia mountains
- Occupation
- Owner/electrical contractor
Got a call from an industrial customer of mine Sunday afternoon, his hydraulic punch was down, and he had 50 doors that needed to go out. He said the motor was buzzing loudly, and would not start. I get there, motor sounded like it was locked up. The coupling was exposed, so I was able to easily check to see if it was free. Pump was free, on to checking the start capacitors (5 hp, 240 volt single phase) all caps including the run caps good. Nameplate is on the backside, clean it off to get the info. Nameplate says 5 hp, 460 volt, THREE Phase. The owner said it was rewound about 18 years ago. It is very apparent the motor guy changed it to single phase, but didn’t change the name plate!