So on the attached SLD, I have a dilemma on X2. But first, I should fill in some details.
Poco supplies power from upper left, via their own HV:480/277wye xfmr. The load comes off via the 200A shunt trip in H1 & down a long $$ cable to a 112.5KVA delta-wye, and some other 3ph 480 loads. No 277 loads.
Also on H1 is an array of grid-tie inverters via the 40A breaker.
When Reddy Kilowatt goes away [too frequently], ATS1 throws and the backup inverters start. The generator offscreen right will start/stop as needed.
My dilemma is X2. I believe we need wye on the LV side because I can't get a statement from the mfgr that they can [not?] drive a delta winding, and because I have local 120VAC loads fed from SL1. [True/false?]
When poco is feeding; their HV secondary provides the ground reference so the 480 legs are not floating wherever they wish vs ground; they are 277 above, period.
But in the other mode, what does that? It's gotta be X2's HV side is a wye.
But I at least was taught that wye-wye was evil... err asking for real problems, harmonic & otherwise, without major spells and chants, invoked under a full moon, etc.
To add complexity, the grid-tie inverters are not just able to produce when the poco is up; but also after the backup units are up & stable. Any surplus shall recharge the backup batteries via the output, now input of the backup inverters. So then X2 is then acting as a stepdown transformer.
I've read of "wild leg" 3ph schemes that ground a corner or a centertap, and of zig-zags, but know only that much. A magnetics guru told me of wye-wye xfmers with an aux. delta winding solely to cancel the harmonics.
So what's the answer here?
Poco supplies power from upper left, via their own HV:480/277wye xfmr. The load comes off via the 200A shunt trip in H1 & down a long $$ cable to a 112.5KVA delta-wye, and some other 3ph 480 loads. No 277 loads.
Also on H1 is an array of grid-tie inverters via the 40A breaker.
When Reddy Kilowatt goes away [too frequently], ATS1 throws and the backup inverters start. The generator offscreen right will start/stop as needed.
My dilemma is X2. I believe we need wye on the LV side because I can't get a statement from the mfgr that they can [not?] drive a delta winding, and because I have local 120VAC loads fed from SL1. [True/false?]
When poco is feeding; their HV secondary provides the ground reference so the 480 legs are not floating wherever they wish vs ground; they are 277 above, period.
But in the other mode, what does that? It's gotta be X2's HV side is a wye.
But I at least was taught that wye-wye was evil... err asking for real problems, harmonic & otherwise, without major spells and chants, invoked under a full moon, etc.
To add complexity, the grid-tie inverters are not just able to produce when the poco is up; but also after the backup units are up & stable. Any surplus shall recharge the backup batteries via the output, now input of the backup inverters. So then X2 is then acting as a stepdown transformer.
I've read of "wild leg" 3ph schemes that ground a corner or a centertap, and of zig-zags, but know only that much. A magnetics guru told me of wye-wye xfmers with an aux. delta winding solely to cancel the harmonics.
So what's the answer here?