We'll have 6 conductors going from the controller to the fire pump. Per 430.22(C) this means our conductors must be 72% of our full load current (FLC). What this article and 695 fail to mention is any derating of the conductors based on >3 current carrying conductors. Don't we need a 80% derate (310.15(B)(3)(a))?