Was playing with a 45 KVA 240 delta -> 208 wye transformer today that was hooked up backwards, before I took it out (this is the one from my thread from half a week ago where we had that meltdown due to a utility phase loss). So just curious about a couple things. With no load connected, and the XO (now primary) floating, I metered 3.5 amps on X1 and X3, and 5.5 amps on X2. IS this typical? Why is the B phase drawing more? When I jumpered the X0 to ground (metal raceway back to primary neutral), I got 40 amps flowing through the bonding jumper, and X1-X3 went up to 16 amps! Wow, I didnt think it would be that much. It was neat to play with this firsthand, now I really know why you must float the X0, although I am not clear on the electrical theory behind it. Does anyone want to take a stab at what exactly happens with the impedance of the windings when the X0 is bonded?
Oh and one addition question: I was curious how much energy this thing as been wasting. Any rough guesses assuming the figures I gave? Having pretty much balance on the phases but 40 amps on the neutral is really throwing me.......