WYe Grounded PTs on Pure delta system

mooreaaryan

Member
Location
Bakersfield CA
Occupation
Electrician
Good morning all
I have a Primary transformer DELTA/DELTA 70KV TO 12KV. within the last five years the facility has added solar to the site with BESS. The old system has a MV distribution of wye delta transformer in the plant and the new system has wye grounded PTs for measuring and the SEL ground fault protection. When we deenergize the system for maintenance or inspection we cannot get the plnat back on line with out deracking the PTs and force the system on


How does the PTs wye grounded and the DELTA system interact? Why does is not consistently interact? How would someone approach fixing this system to ensure its safety and operations
 
Is that typical to have grounded wye PT's on an ungrounded system? Doesnt that ground the system or at least effect your fault detection scheme?
I have not done enough MV Microgrid to Existing facilities to know if this is typical. I understand that the grounded wye PTs are needed to ensure the Ground Fault Protection scheme has a reference to ground to engage protection.
 