JuliaTruchsess
- Newtown, CT, USA
- Engineer
My client is bidding on inclusion of their equipment as part of a larger installation, and I'm "helping" spec/source some of the ancillary equipment such as transformers. The POCO delivers (presumably) MV delta to a transformer whose secondary is 480Y/277. This goes to a service-entrance-rated 4-pole ATS whose other source is a separately-derived generator. From the ATS, they run the 480Y/277 to various equipment around the site, which is outside our/my scope of involvement.
My client's equipment (ITE) requires 208Y/120. 408 delta / 208 wye transformers are obviously very common, and I'm pretty sure I could just hook one up to the line legs of the 480 wye (right?), but the question is: what to do about neutral on the secondary side of my 208Y/120? And even if I could find a 408 wye primary, this would still be the question. Can/should I just run a solid neutral tying the 480Y system's N to the 208Y's N? The alternative would seem to be creating another SDS at the 208 secondary, but having two different neutrals running around the same facility does not sound like a good idea.