Volta
- Columbus, Ohio
Three old single phase transformers, 120 primary, 120/240 secondary. 25 kVA each. Wired as 208/120 wye primary, 240 high-leg delta secondary. They feed a 200(225) amp panel.
Wired wrong in a few different ways now. Among other problems, the primary and secondary ties are #4 and #3, respectively. Line and load are 3/0, which is ok. One tie for the primary neutral is severely overheated. I want to remove the entire bank. The transformers are too small to use the proper wire and lugs. The customer can live without the delta system.
The panel it feeds (circa 1969) is a SqD NQOB delta panel. It has 52 spaces, bottom feed, three phase only on the lower 18 or so spaces, then only phase A and C extending to the upper part. It has a regular SqD label that says 240 volt delta on it.
I would like to feed this directly from the 208/120 volt building system. I am ok with the voltage change, electrically [110.4, 240.83(E)].
Could it be that instructions exist(ed) for this panel that would require is use only on a delta system [110.3(B)]? It is obvious that is what it was made for, and is labeled that way.
Should it pass inspection as 208 wye?