mblackway@bradleyelectro.
Member
- Location
- Delaware
- Occupation
- Electrical Sales
I have a 1000KW generator feeding 277/480 wye to a step-up transformer, to 13.8kv primary delta. Once we leave the transformer and go to some switchgear, we have voltage fluctuating mostly on A phase. B phase and C phase are a little high on our readings at the switchgear through our processor. Everything on the switchgear was changed out. This was originally caused by too small of arrestors that blew on startup and a ground wire that was not tightened from the transformer. We have tried to lift the neutral and bond on the XO terminal, but we still get the same readings. Could the 1/0 ground wire be too small, and could there be a difference in potential between the grounding counterpoise of the transformer pad and the counterpoise of the switchgear? It seems as though we are hunting for a reference, but I cannot pinpoint the problem.