Wye Transformer - Secondary

Status
Not open for further replies.

DMG_1

Member
Location
Boston, MA, USA
Hi All.

I am making the transition from the low voltage world to the medium voltage world. I have two situations where I have a Utility Transformer as the source, Delta (Primary) - Wye (Secondary). In the first case we are feeding a 4160 Switchgear which inturn feeds multiple outdoor substations. In the second case I am feeding multiple indoor substations. In the low voltage world I would always pull a neutral because I was feeding power / lighting panels. In both of the cases above I am being told that we will not be pulling a neutral. Can anyone tell me as to when a Neutral would be required from a Wye Secondary and advantages / disadvantages as to pulling one?

Thanks.
 

bob

Senior Member
Location
Alabama
If the primary to the transformer is delta connected there is no need for a neutral. You will need to install an EGC for the transformer.
 

templdl

Senior Member
Location
Wisconsin
Bob is right on. It is not uncommon for some to think that should you have a wye secondary the primary of a down stream transformer must be a wye also which is not correct, I have found the wye primaries are more apt to be used by utilities.
 

jghrist

Senior Member
Hi All.

I am making the transition from the low voltage world to the medium voltage world. I have two situations where I have a Utility Transformer as the source, Delta (Primary) - Wye (Secondary). In the first case we are feeding a 4160 Switchgear which inturn feeds multiple outdoor substations. In the second case I am feeding multiple indoor substations. In the low voltage world I would always pull a neutral because I was feeding power / lighting panels. In both of the cases above I am being told that we will not be pulling a neutral. Can anyone tell me as to when a Neutral would be required from a Wye Secondary and advantages / disadvantages as to pulling one?

Look at it this way. If all of the loads are connected phase-to-phase or to a delta winding (that has no neutral), then if you pulled a neutral, nothing would be connected to it. If that's the case, it has no purpose. You need an EGC in case there is a phase-to-ground fault to carry the fault current back to the source.
 

Shoe

Senior Member
Location
USA
Yep, only pull a neutral if you need one. To translate to your low-voltage experience, think of it as a 480V, 3-wire distribution to a motor control center that might feed all 3-phase loads and a few delta-wye transformers. You wouldn't be inclined to pull a neutral in that case either.
 