Open Neutral
Senior Member
- Location
- Inside the Beltway
- Occupation
- Engineer
I was at the Orlando Fairgrounds recently. There's some newish rule that the carnival rides visiting periodically must run off POCO, not Diesel, power. Hence, there are a lot of poles with 3 unlittle pigs on each. At their base is a locked panel that the rides will be hardwired to; as well as duplex outlets.
They won't run out of capacity; there's a major substation adjacent to the property.
Comments?
They won't run out of capacity; there's a major substation adjacent to the property.
- Why would two of the pigs be bigger than others? I saw that twice. I'm aware of open neutral configurations but this isn't.
- As far as I could tell, the transformers were wired wye-wye. That makes little sense to me, who was taught that you need delta somewhere to keep the 3rd harmonics in check. I don't know if the pictures are good enough to see same, but I felt sure I saw a bare jumper on at least 2 poles, joining 3 primary terminals.
Comments?