Two things I've always held to:
1) Neutral and Equipment Grounding conductor are bonded at Service panel (point of origination) and NEVER to meet again.
2) With transformers creating a Newly Derived system, Neutral and Equipment Grounding conductor are Bonded at Secondary ONLY.
Have run into a situation with the manufactures diagram/instructions on a wye wye transformer. It is calling for the Primary & Secondary Neutral to be"Tied" together and both Primary & Secondary are both bonded to chassis ground. (equipment ground)
My Boss called the Manufacture and they insist this is correct. To me this seems to go against the concept of an isolation transformer. Is a Wye Wye not an "Isolation" transformer?
1) Neutral and Equipment Grounding conductor are bonded at Service panel (point of origination) and NEVER to meet again.
2) With transformers creating a Newly Derived system, Neutral and Equipment Grounding conductor are Bonded at Secondary ONLY.
Have run into a situation with the manufactures diagram/instructions on a wye wye transformer. It is calling for the Primary & Secondary Neutral to be"Tied" together and both Primary & Secondary are both bonded to chassis ground. (equipment ground)
My Boss called the Manufacture and they insist this is correct. To me this seems to go against the concept of an isolation transformer. Is a Wye Wye not an "Isolation" transformer?