Don't get the cart before the horse.
1. Conductors are sized based on the load per 310.
2. Overcurrent protection is sized based on the conductors per 240.
3. The transformer is sized any way you want.
4. Transformer protection is sized per 450, the overcurrent protective device chosen in step 2, may be used to meet the requirements of 450.