X/R ratio for transformers
mbrooke
Batteries Included
United States
Technician
Question. How does unit size effect X/R?
Picture two scenarios.
1. 115kv to 34.5kv Dyn1 120MVA unit
2. 3 115kv to 34.5kv Dyn1 40MVA units run in parallel
In general, would I have the same X/R for both scenarios or would #2 be higher in resistance while being lower in reactance? If so how does this effect my fault current outcome?
Transformer reactance[X] depends on leakage magnetic flux and indirect on transformer impedance. X=SQRT(Z^2-R^2).
Transformer resistance[R] depends on copper losses[Pcu] R=sqrt(Pcu/I^2/3).
The transformer performance could be different in order to comply with the specification as short-circuit impedance connected with maximum short-circuit allowable and the losses which are
connected with the losses prices versus copper conductor price.
ANSI Standard C37.010 recommends the usual X/R ratio.
For instance for 120 MVA it has to be about 40 and for 40 MVA about 28.
But for a typical order, what would be more X/R?
Question, would Pcu not be P=(I^2xR) x 3.14?
That is quite the same quotation from ANSI C37.010 I said about.
He's got a common wound 120 MVA 3 ph
and 3 each 40 MVA 1 ph configured as a 120 MVA 3 ph bank
a rough approximation 3 ph to 1 ph equivilent
the 3 phase ~ 41
the 3 1 phase sqrt3 x 26 ~ 45
the x/r is phase ang
the delta between 41 and 45 is 0.12 deg, moot
R has to be similar since i is the same
Xl (L) must be close since same power is transformed
the 3 phase ~ 41
Close, 3, three phase 40MVA. That way on unit can be taken out of service and the remaining two still carry 80MVA of load.