Question. How does unit size effect X/R?

Picture two scenarios.

1. 115kv to 34.5kv Dyn1 120MVA unit

2. 3 115kv to 34.5kv Dyn1 40MVA units run in parallel

In general, would I have the same X/R for both scenarios or would #2 be higher in resistance while being lower in reactance? If so how does this effect my fault current outcome?
 

Julius Right

Senior Member
Occupation
Electrical Engineer Power Station Physical Design Retired
Transformer reactance[X] depends on leakage magnetic flux and indirect on transformer impedance. X=SQRT(Z^2-R^2).
Transformer resistance[R] depends on copper losses[Pcu] R=sqrt(Pcu/I^2/3).
The transformer performance could be different in order to comply with the specification as short-circuit impedance connected with maximum short-circuit allowable and the losses which are
connected with the losses prices versus copper conductor price.
ANSI Standard C37.010 recommends the usual X/R ratio.
For instance for 120 MVA it has to be about 40 and for 40 MVA about 28.
 

mbrooke

Batteries Included
Location
United States
Occupation
Technician
Transformer reactance[X] depends on leakage magnetic flux and indirect on transformer impedance. X=SQRT(Z^2-R^2).
Transformer resistance[R] depends on copper losses[Pcu] R=sqrt(Pcu/I^2/3).
The transformer performance could be different in order to comply with the specification as short-circuit impedance connected with maximum short-circuit allowable and the losses which are
connected with the losses prices versus copper conductor price.
ANSI Standard C37.010 recommends the usual X/R ratio.
For instance for 120 MVA it has to be about 40 and for 40 MVA about 28.

Thanks :)

But for a typical order, what would be more X/R?

Question, would Pcu not be P=(I^2xR) x 3.14?
 

Ingenieur

Senior Member
Location
Earth
That is quite the same quotation from ANSI C37.010 I said about.

He's got a common wound 120 MVA 3 ph
and 3 each 40 MVA 1 ph configured as a 120 MVA 3 ph bank
a rough approximation 3 ph to 1 ph equivilent
the 3 phase ~ 41
the 3 1 phase sqrt3 x 26 ~ 45

the x/r is phase ang
the delta between 41 and 45 is 0.12 deg, moot

R has to be similar since i is the same
Xl (L) must be close since same power is transformed
 

mbrooke

Batteries Included
Location
United States
Occupation
Technician
He's got a common wound 120 MVA 3 ph
and 3 each 40 MVA 1 ph configured as a 120 MVA 3 ph bank
a rough approximation 3 ph to 1 ph equivilent
the 3 phase ~ 41
the 3 1 phase sqrt3 x 26 ~ 45

the x/r is phase ang
the delta between 41 and 45 is 0.12 deg, moot

R has to be similar since i is the same
Xl (L) must be close since same power is transformed


Close, 3, three phase 40MVA. That way on unit can be taken out of service and the remaining two still carry 80MVA of load.
 