hhsting
- Glen bunie, md, us
- Junior plan reviewer
Would EPO push button in readily accessible location in control room provided by manufacturer count as xray disconnect or not?
			Waht code section are you referencing?
Don;A control button is never a disconnect, even one that operates a shunt trip breaker. A disconnect is a device that directly opens the circuit conductors. The code section you cited requires a disconnect. You cannot use an emergency stop button or other control device to comply with that section.
If it ultimately ends up controlling the shunt coil to a shunt trip breaker there is nothing wrong with using it to open the breaker. But if you follow most any safety policy you still need to verify the power is off and lock the breaker if you turned it off for the reason of working on the equipment.Don;
Is there any provision for e-stop that would count? There's a lot of equipment where just pulling a disconnect is
rude. But given a few microseconds or tenths of a seconds, the equipment can shut down cleanly and shed load without sparking or whatever.
If the requirement is for a disconnect, there is no place where a control device can substitute for the required disconnect. However is it common to use both. The disconnect is for lockout tag out when working on the equipment and the control device is for normal or emergency shutdown.Don;
So lets's say I had a big red button for "safe shutdown" initiates a clean shutdown situation: saving state, turning off motors or loads, reducing spark potential... but it also triggers a timeout. Two seconds after the big red button is pushed it will activate the shut coil no matter what.A control button is never a disconnect, even one that operates a shunt trip breaker. A disconnect is a device that directly opens the circuit conductors. The code section you cited requires a disconnect. You cannot use an emergency stop button or other control device to comply with that section.
As mentioned E-stop is for controls. This may get more into other regulations besides NEC as to how rapidly it must shut down once the E-stop is pressed. Otherwise yes a simple delay timer between the E-stop button and shunt coil or whatever other controls are needed for a programmed shutdown process could be placed in the control circuit with a final order of operations to energize the shunt coil. I wouldn't think there is much to most x-ray machines to shut down in an orderly fashion though. Maybe if there is moving patient exam table or something of that nature that also gets shut down, though that may be more common for more advanced medical imaging like CT or MRI machines.So lets's say I had a big red button for "safe shutdown" initiates a clean shutdown situation: saving state, turning off motors or loads, reducing spark potential... but it also triggers a timeout. Two seconds after the big red button is pushed it will activate the shut coil no matter what.
Is there a way to build that, under the NEC? A combination e-Stop and disconnect?
Or a shunt breaker with a touch sensor: the moment it's touched it initiates e-Stop, faster than a human hand could yank the breaker handles.
Where in the code is use of control button for a disconnect precluded?
Article 100 Disconnecting Means" reads "A device, or group of devices, or other means by which the conductors of a circuit can be disconnected from their source of supply. (CMP-1)".
Then "Article 100 switching device" further defines isolating switches.
Article 110.25 defines "Lockable disconnecting means". And 230.85 is all about marking.
Because the disconnect itself must open the circuit conductors.So lets's say I had a big red button for "safe shutdown" initiates a clean shutdown situation: saving state, turning off motors or loads, reducing spark potential... but it also triggers a timeout. Two seconds after the big red button is pushed it will activate the shut coil no matter what.
To be precise, where does that come into the code?Because the disconnect itself must open the circuit conductors.
You can use the E-stop, as long as there is a physical way to operate, and in most cases, lockout, the actual disconnect.
Exactly. The problem with a big red mushroom button on the wall is that no one knows how it works or what it disconnects. With a disconnect, you can open the cover and see the contacts open and use you meter to verify that the load side is deenergized.The device itself must physically open the conductors.
Circuit breaker or molded case switch can't always visually see the contacts.With a disconnect, you can open the cover and see the contacts open
Refer to the definitions for "readily accessible".NEC 2017 Article 517.72