Hi,
we have 135 KVA, X-Ray machine in the Hospital with 380V 3phase supply.
we do not have any other data about the momentary rating or the long time rating, so we considered the long time rating for sizing, so 135000/380/1.732 = 205 Amps
so, as per 660.6, the ampacity of the circuit shall not be less than 100% of the long-time rating ( which we do not have) it will be 205A.
and from table 310.15(B).16 75C column(because more than 100A as per 110.14.(C).1.(b), for terminal Temperature limitations ) we have to use 3/0 conductors and (as per Table 240.6(A)) 200A Circuit Breaker is selected.
and as per table 250.122 the size of Equipment Grounding Conductor (EGC) is 6 AWG.
please note that Voltage drop, temperature correction factor, or Conductor Bundling adjustment will not affect my selection as per site condition.
so as a summary, I will pull 4x3/0 copper conductor (4 cores cable) + 6 AWG green yellow conductor for grounding.
My questions are:
1-Is the above sizing is right?
2-As per my knowledge X-Ray machines is considered as a nonlinear load, so, we can't use reduced neutral as per 310.15.(B).(5).(c), am I right? if the answer is no, how to size the neutral for the x-ray machine?
but if the answer is yes, so the neutral conductor will be counted as a Current Carrying Conductor (CCC), so Conductor Bundling Adjustment factor shall be applied, because we are going to have 4 CCC, am I right?
Thanks for reading all this.
Regards,
Ammar M. I.
we have 135 KVA, X-Ray machine in the Hospital with 380V 3phase supply.
we do not have any other data about the momentary rating or the long time rating, so we considered the long time rating for sizing, so 135000/380/1.732 = 205 Amps
so, as per 660.6, the ampacity of the circuit shall not be less than 100% of the long-time rating ( which we do not have) it will be 205A.
and from table 310.15(B).16 75C column(because more than 100A as per 110.14.(C).1.(b), for terminal Temperature limitations ) we have to use 3/0 conductors and (as per Table 240.6(A)) 200A Circuit Breaker is selected.
and as per table 250.122 the size of Equipment Grounding Conductor (EGC) is 6 AWG.
please note that Voltage drop, temperature correction factor, or Conductor Bundling adjustment will not affect my selection as per site condition.
so as a summary, I will pull 4x3/0 copper conductor (4 cores cable) + 6 AWG green yellow conductor for grounding.
My questions are:
1-Is the above sizing is right?
2-As per my knowledge X-Ray machines is considered as a nonlinear load, so, we can't use reduced neutral as per 310.15.(B).(5).(c), am I right? if the answer is no, how to size the neutral for the x-ray machine?
but if the answer is yes, so the neutral conductor will be counted as a Current Carrying Conductor (CCC), so Conductor Bundling Adjustment factor shall be applied, because we are going to have 4 CCC, am I right?
Thanks for reading all this.
Regards,
Ammar M. I.