Can someone please advise whether or not to connect X0 to the frame for a Siemens 75 KVA delta-wye?
Primary is 3 phase 480 with no neutral and secondary is 240-120 3 phase with neutral to 42 CB panelboard. Service is feeding an office area with separate, insulated ground bar in panel for computer outlets. Transformer primary is fed with 480 conducters using 2 awg wire from Siemens/ITE bus plug and an 8 awg ground - no neutral to delta. Secondary is 4/0 3 phase and neutral to 250 amp panelboard with 6 awg ground.
Panelboard has separate 6 awg ground back to fusible bus plug for isolated ground bar in panelboard. Isolated ground ran through its own 3/4 inch conduit, separate from the 4/0 feed ground wire.
I hooked up a bonding wire for X0 to the xmfr frame using 30 inches of left-over 4/0 cable (NEC table 250.66 said to use 2 awg or larger).
I also bonded the panelboard netural to the panelboard frame, using the included green bond screw.
Are these measures correct? Thanks for helping out an instrument and automation guy on his first commercial electrical job! Every time I read the NEC I get a different meaning and just need an expert to verify my thinking.
Regards,
Andy
P.S. Is it also okay to mount the insulated ground bar on the bottom of the CB panelboard, as opposed to the back plane? I wish to have the insulated ground bar centered in the panel; to facilitate connecting insulated computer outlet grounds from either side of the breaker rows.
Primary is 3 phase 480 with no neutral and secondary is 240-120 3 phase with neutral to 42 CB panelboard. Service is feeding an office area with separate, insulated ground bar in panel for computer outlets. Transformer primary is fed with 480 conducters using 2 awg wire from Siemens/ITE bus plug and an 8 awg ground - no neutral to delta. Secondary is 4/0 3 phase and neutral to 250 amp panelboard with 6 awg ground.
Panelboard has separate 6 awg ground back to fusible bus plug for isolated ground bar in panelboard. Isolated ground ran through its own 3/4 inch conduit, separate from the 4/0 feed ground wire.
I hooked up a bonding wire for X0 to the xmfr frame using 30 inches of left-over 4/0 cable (NEC table 250.66 said to use 2 awg or larger).
I also bonded the panelboard netural to the panelboard frame, using the included green bond screw.
Are these measures correct? Thanks for helping out an instrument and automation guy on his first commercial electrical job! Every time I read the NEC I get a different meaning and just need an expert to verify my thinking.
Regards,
Andy
P.S. Is it also okay to mount the insulated ground bar on the bottom of the CB panelboard, as opposed to the back plane? I wish to have the insulated ground bar centered in the panel; to facilitate connecting insulated computer outlet grounds from either side of the breaker rows.