X10 sensor around neutral

Status
Not open for further replies.

GG

Senior Member
Location
Ft.Worth, T.X.
I was in a residential panel today replacing an AFCI breaker. I noticed wrapped around the neutral wire was an X10 sensor. It had 3 wires, 1 landed on the neutral bus and 2 landed on a 2 pole breaker. What is this sensor? Does anyone have a link to the directions for it or nay inof I can study about it?
 
It is a phase coupler, to jump the X-10 signals across both legs, other wise the X-10 signal will not be able to talk to devices on the other leg because of the transformer, if the transformer is close to the house sometimes they will cross over, but if the transformer is at a distance then this crossover will help.


More INFO
 
Last edited:
Thanks Hurk. The new owner of the house wanted it removed. I said I better find out what it does before I just remove it. What will removing it do, make the whole X10 system inoperable?
 
Not completely. All X10 devices on each leg will be able to talk to each other, but X10 devices on one leg won't be able to talk to X10 on the other leg. If they have a central controller, some devices will work and some won't.

Don't remove it unless they've abandoned the X10 system, or at least have abandoned centralized control.
 
Thanks Hurk. The new owner of the house wanted it removed. I said I better find out what it does before I just remove it. What will removing it do, make the whole X10 system inoperable?

Yes it will cause some of the devices to not receive the proper commands, it shouldn't be mounted in the panel, it should be put in a device box which is then wired to the panel, since this device has no low voltage wire it would be hard pressed to find a code to disallow it, but in most areas inspectors don't want to see them in a panel.

Generally they are placed in a two gang box with a blank cover, and short piece of 14/3 is ran to the panel and landed on a 2-pole 15 amp breaker, this is explained in the article I posted a link to.
 
Not completely. All X10 devices on each leg will be able to talk to each other, but X10 devices on one leg won't be able to talk to X10 on the other leg. If they have a central controller, some devices will work and some won't.

Don't remove it unless they've abandoned the X10 system, or at least have abandoned centralized control.

It doesn't always have to be a central controller type system for you to have problems with X-10, many times you will have switches on one leg and the switched load on another, so the effects of removing the phase coupler can cause many switches to stop working.

A funny thing happened in one case, I had installed 4 switches to control a new flood light that was up at the peek of the gable of a 3 story house, to light up the back yard, the switches were on the main level, everything was working just fine when I left, thought to myself "cool no phase coupler needed", but what I didn't realize was the home owner was doing laundry and both her electric dryers was on when I tried the system out, after I was gone and when she was done with her laundry and the dryers were off, the system stopped working, well the electric elements in the dryers was linking the two legs together and allowing the X-10 signal to cross over, boy did I feel dumb, had to add a phase coupler and everything worked just fine.

Also just a heads up, sometimes if you are having a problem getting a signal in a room, look around for a surge suppressor strip on that circuit, if it has a RFI filter in it, it can block the X-10 signals on the whole circuit, and even the whole phase if close enough to the panel.
 