Small renovation job, installing a Xmfr but the source panel (480/277V, 3Ph, 4w) seems to be using the RGSC as the grounding means; the EGCs are all disconnected, "waiting to be connected. No grounding bar.
The Question: Can we install a grounding bushing w/ locknut to establish the grounding bar, connect the Xfmr and all the EGCs? See picture. grounding.jpg
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Well the question is, by installing a grounding bushing and locknut, are we satisfying the grounding requirements for the source panel? If that is Kosher, then yeah, I would dedicate the Xfmr EGC to 1 bar.
So you want to attach the EGC feeding the transformer primary to a bonding bushing?
 