Were setting a 480/120/208 xfmr for a small deli, 45kva xfmr is fed from a 480 volt 80 amp breaker (all three phase), secondary is three phase 125 amp breaker.Primary wire is #2 secondary is #1/0 thhn.Surrounding structure is all concrete (no steel) Electric room has a ground grid but it would take drilling two feet of concrete to make it an excessable place to ground( it's about sixty feet away).There is a small bathroom with cold water (copper), of course I dont know if its a good path of copper back to the Main valve (continuity?).
My question is what alternative do I have for grounding my xfmr neautral, Would the bathroom cold water suffice, or should I plan on drilling the two feet of concrete to reach the building ground.
I am on grade so a ground rod would be a possibilty, however I'd rather not drill the floor due to high voltage feeders,cathodic protection and or plumbing issues...
I've set seperatly derived systems many times before, but never had such a hard time finding a building ground.
Thanks
My question is what alternative do I have for grounding my xfmr neautral, Would the bathroom cold water suffice, or should I plan on drilling the two feet of concrete to reach the building ground.
I am on grade so a ground rod would be a possibilty, however I'd rather not drill the floor due to high voltage feeders,cathodic protection and or plumbing issues...
I've set seperatly derived systems many times before, but never had such a hard time finding a building ground.
Thanks