Please review my calculations and let me know if this is correct or way off. I will try to include everything i have. The goal is to add a transformer and panel for a lunch room with the following circuits.
(1) two-120v outlets tied together
(2) five separate 120v outlets for 5 refrigerators
(3) 240v outlet for oven-40A breaker (4300watt)
(4) 240v outlet for stove-50A breaker (3700watt)
(5) 240v outlet for small under counter water heater
(6) 120v outlet for vent-a-hood
(7) two-120v outlets tied together
(8) 120v outlet for a microwave
(9) two-120v outlets tied together with a microwave on one of the outlets.
Total of 13 separate circuits. (planned for 15-20A breakers for the rest of the circuits)
Originally the plan was to have a 15kVA single phase 480-120/240V xfmr, 70A primary ocp & 70A secondary ocp. However the question was posed if it was too small. Below i have done the calcs for a larger 37.5kVA xfmr. are my calcs correct? or is this way over sized?
Any feed back on this would be greatly appreciated. I dont have the current draw on the appliances but hoping there may be some more experience here to have a better idea of what is realistic. The cable sizing seems a bit large for this type of application but thats just my initial thoughts. i dont want to oversize this if possible. The next size down transformer is a 25kVA i could use if needed.
- 37.5KVA 480V-120/240V single phase 3-wire transformer.
- Primary amps- 37.5KVA / 480V = 78.125A
- Primary OCP per table 450.3 (B) can be up to 2.5 X the primary amps.
- In this scenario, the XFMR is close to MCC so I will do higher % . I'll use 224% (2.24X) so the primary OCP breaker will be 175A
- Secondary amps - 37.5KVA / 2 = 18.75KVA ( this is because it’s a 3-wire system so 2 120V legs split the KVA value.
- So 18.75KVA / 120V = 156.25A or (37kVA / 480 = 156.25A)
- Secondary OCP per table 450.3 (B) can be up to 1.25 X the secondary amps
- For this application we will be using 240V and 120V circuits so at 1.25 * 156.25A = 195.3125A OCP
- This can be rounded down to a 175A breaker for the secondary
- The conductors for the primary and secondary will be rated 1.25 X the primary and secondary OCP to get the amperage needed for the wire (215.3).
- So ( both are 175A) 175A X 1.25 = 218.75A .
- The conductors used in this situation must be rated at or above 218.75A. (uglys book is a 3/0 cable)