chevyx92

Senior Member
Location
VA BCH, VA
A 150KVA with 480v 3 phase input. 150000/830= 180.722 Amps. My question is since 180 is not a standard rating in 240.6(A), can you got to a 200A breaker if calculated load is less than 180.722 Amps? Or do I need to drop down to a 175A breaker?
 
If you size the OCPD at 175, it will most likely trip on the inrush current. Assuming that there is secondary protection the primary OCPD can be 250% of the primary current. That would be 451 amps...you can't round up so you could use a 450 amp OCPD. If there is no secondary protection you can go up to 125% of the primary current and in this case you can round up to the next standard size, which would permit you to use a 250 amp OCPD. Note that the conductors between the primary OCPD and the transformer must have an ampacity equal to or greater than the rating of the primary OCPD.
 