S Steelhead Senior Member Location Southeastern Wisconsin Occupation Industrial Maint/Journeyman Jan 7, 2014 #1 Can the OCPD for the secondary of a XFMR also serve as the branch circuit protection?
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Jan 7, 2014 #2 certainly can
J jim dungar Moderator Staff member Location Wisconsin Occupation PE (Retired) - Power Systems Jan 7, 2014 #3 You could read article 450.3 as based on using the branch feeder protection as the transformer secondary protection. Conductor protection is a requirement. Transformer secondary protection is optional.
You could read article 450.3 as based on using the branch feeder protection as the transformer secondary protection. Conductor protection is a requirement. Transformer secondary protection is optional.
S Steelhead Senior Member Location Southeastern Wisconsin Occupation Industrial Maint/Journeyman Jan 7, 2014 #4 Thanks guys. Your answers affirmed what I was thinking.