I have 112.5 KVA transformer that feeds (4) tapped lighting and appliance panelboards from the secondary. Which NEC table should be utilized for sizing the panelboard equipment grounds? (250.66 or 250.122)
Presuming you are creating a new Separately Derived System with this transformer, there will have to be a connection between neutral and ground somewhere nearby. The wire that goes from that point to planet Earth is sized by 250.66. Equipment grounding conductors are sized by 250.122.
One the primary side you would use 250.122 to size the EGC in the feeder. On the secondary side you would use 250.66 to size the GEC, the equipment bonding jumper and the system bonding jumper.