B Bob49 Member Location Kemp tx May 19, 2020 #1 Using the 25 ft. rule for the total combined length, can the primary conductors be two thirds of that length ? Thanks for any replies.
Using the 25 ft. rule for the total combined length, can the primary conductors be two thirds of that length ? Thanks for any replies.
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician May 19, 2020 #2 Are you referring to 240.21(B)(3)?
B Bob49 Member Location Kemp tx May 19, 2020 #3 infinity said: Are you referring to 240.21(B)(3)? Click to expand... Thank you Infinity. Yes 240.21 (B) (3). To have the transformer in the ideal spot, we need about 16 feet on the primary and only about 6 on the secondary.
infinity said: Are you referring to 240.21(B)(3)? Click to expand... Thank you Infinity. Yes 240.21 (B) (3). To have the transformer in the ideal spot, we need about 16 feet on the primary and only about 6 on the secondary.