Recently I looked at a transformer that kept tripping the breaker feeding it. The transformer is a 45 kva 480/277 3ph to 208 3ph with no X0 terminal. Originally the transformer feed a panel with four 208 3ph breakers. The transformer housing is bonded to building steel with a #6 solid. This was installed around 40 years ago.
About 20 years ago one of the 208 3ph breakers was used to feed a 208/120 3ph panel. FMC was run from the transformer to the 208/120 3ph panel. The Ground wire from the line side disconnect was removed from the grounding terminal in the transformer and spliced to the grounded conductor from the 208/120 3ph panel. This is a direct path back to the MDP.
The problem I found is the mechanical lug connected to building steel had become loose and was arcing.
How does this work? My guess is the "neutral" path is from the 208/120 3ph panel to the MDP then to building steel and then from building steel to the transformer housing and then finally to the transformer.
About 20 years ago one of the 208 3ph breakers was used to feed a 208/120 3ph panel. FMC was run from the transformer to the 208/120 3ph panel. The Ground wire from the line side disconnect was removed from the grounding terminal in the transformer and spliced to the grounded conductor from the 208/120 3ph panel. This is a direct path back to the MDP.
The problem I found is the mechanical lug connected to building steel had become loose and was arcing.
How does this work? My guess is the "neutral" path is from the 208/120 3ph panel to the MDP then to building steel and then from building steel to the transformer housing and then finally to the transformer.