:-? Under 240.21(C )(2).1.b it states that the conductor ampacity ?is not less than the rating of the device supplied by the secondary conductors or not less than the rating of the overcurrent-protective device at the termination of the secondary conductors? the code also states that 240.4(B) shall not be permitted for transformer secondary conductors.
With all that being stated if you had a delta / wye 112.5 (480Δ-208Y/120V, 3?-4W+GRD) primary fla = 135A, secondary = 312.5 @ 125% = 390 = 400A breaker. So in this case the terminations on the breaker are only rated for 75?C.
Now for the question:
Can I use the ampacity of the 90?C conductor specified seeing that the ampacity of the conductor is rated at 90?C or do I have to use the 75?C column because the terminations are only rated for the 75?. So does this mean that I can use the 90?C ampacity rating so long as my load does not exceed the 75?C rating? For the 400A would I be safe running 500Kcmil (430A@ 90? / 380A@75?) or do I need to run parallel 3/0?s (225A@90? / 200A@75?) only because the standard breaker will not accept anything larger than a 500Kcmil so running one set of 600Kcmil will not work? I have been asking around my office and seem to get differing opinions and would like to hear everyone else?s views on the subject. Maybe I am just being to picky??
With all that being stated if you had a delta / wye 112.5 (480Δ-208Y/120V, 3?-4W+GRD) primary fla = 135A, secondary = 312.5 @ 125% = 390 = 400A breaker. So in this case the terminations on the breaker are only rated for 75?C.
Now for the question:
Can I use the ampacity of the 90?C conductor specified seeing that the ampacity of the conductor is rated at 90?C or do I have to use the 75?C column because the terminations are only rated for the 75?. So does this mean that I can use the 90?C ampacity rating so long as my load does not exceed the 75?C rating? For the 400A would I be safe running 500Kcmil (430A@ 90? / 380A@75?) or do I need to run parallel 3/0?s (225A@90? / 200A@75?) only because the standard breaker will not accept anything larger than a 500Kcmil so running one set of 600Kcmil will not work? I have been asking around my office and seem to get differing opinions and would like to hear everyone else?s views on the subject. Maybe I am just being to picky??