Never came across this many, and this size, conduits landing in a xfrmr. Is it even possible(Obviously I assume)? Do they make 5" FMC? Thanks


1760123274583.png
 
4"is the largest FMC but you can't use FMC outside. I have never seen any type of flexible conduit used with a transformer of that size.
Also not sure why they specified 5" conduit. There is a huge jump in costs over 4" and five 600 kcmil fit in a 4"

What about the secondary side?
 
No there is no 5" FMC but with transformer this size you would typically run the RMC right into it.
Imagine lb would be easier
4"is the largest FMC but you can't use FMC outside. I have never seen any type of flexible conduit used with a transformer of that size.
Also not sure why they specified 5" conduit. There is a huge jump in costs over 4" and five 600 kcmil fit in a 4"

What about the secondary side?