Imagine lb would be easierNo there is no 5" FMC but with transformer this size you would typically run the RMC right into it.
4"is the largest FMC but you can't use FMC outside. I have never seen any type of flexible conduit used with a transformer of that size.
Also not sure why they specified 5" conduit. There is a huge jump in costs over 4" and five 600 kcmil fit in a 4"
What about the secondary side?
You can't fit that wire in a standard LB. You will need a mogul one, and you need to make sure it is suitable for that wirefill.Imagine lb would be easier