Xfrmr Feed

Status
Not open for further replies.

kwired

Electron manager
Location
NE Nebraska
A quick look says:

C2-maybe

C4-no

C6-no
I think C4 is a maybe. One could have more then one set of tap conductors leave the transformer in that situation but each set must end in an individual overcurrent device.

One must also consider that for other then two wire single phase systems or three phase three wire delta systems - you usually need to pay attention to transformer secondary overcurrent protection in those cases where you could supply more then one overcurrent device.
 

jumper

Senior Member
I think C4 is a maybe. One could have more then one set of tap conductors leave the transformer in that situation but each set must end in an individual overcurrent device.

One must also consider that for other then two wire single phase systems or three phase three wire delta systems - you usually need to pay attention to transformer secondary overcurrent protection in those cases where you could supply more then one overcurrent device.

I wlll go back and look at C4.

OP does not usually seem to work on the two wire set ups so I did not include it or industrial.
Kinda guessing maybe 480-208/120 till he posts more info.

Could be outside also I suppose.

Need more info.
 

kwired

Electron manager
Location
NE Nebraska
I wlll go back and look at C4.

OP does not usually seem to work on the two wire set ups so I did not include it or industrial.
Kinda guessing maybe 480-208/120 till he posts more info.

Could be outside also I suppose.

Need more info.
I agree it is likely 480 - 208/120. Such system will need secondary protection, but doesn't have to be a single device. 25 foot tap and the outdoor tap must end in an individual overcurrent device, but nothing says you can't have multiple taps off the transformer either.

Two issues here, transformer secondary protection and overcurrent protection for the tap conductor(s).
 