mstrlucky74
Senior Member
- Location
- NJ
Can you have a 45kva xfrmr feed two different panels?Thought it could only feed one load. Thanks.
Depends.
240.21(C) has 6 scenarios.
How long are the secondary conductors?
What type of loads? Panels?
Need more info.
I think C4 is a maybe. One could have more then one set of tap conductors leave the transformer in that situation but each set must end in an individual overcurrent device.A quick look says:
C2-maybe
C4-no
C6-no
I think C4 is a maybe. One could have more then one set of tap conductors leave the transformer in that situation but each set must end in an individual overcurrent device.
One must also consider that for other then two wire single phase systems or three phase three wire delta systems - you usually need to pay attention to transformer secondary overcurrent protection in those cases where you could supply more then one overcurrent device.
I agree it is likely 480 - 208/120. Such system will need secondary protection, but doesn't have to be a single device. 25 foot tap and the outdoor tap must end in an individual overcurrent device, but nothing says you can't have multiple taps off the transformer either.I wlll go back and look at C4.
OP does not usually seem to work on the two wire set ups so I did not include it or industrial.
Kinda guessing maybe 480-208/120 till he posts more info.
Could be outside also I suppose.
Need more info.
Can you have a 45kva xfrmr feed two different panels?Thought it could only feed one load. Thanks.