A Alwayslearningelec Senior Member Location NJ Occupation Estimator Nov 11, 2022 #1 Is there NEC code regarding how far a transformer can be from the primary OCPD? I want to mount xfrmr 40' away from panel feeding it.
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Nov 11, 2022 #2 No requirement on distance other than if it's not "in sight from" it needs to be lockable.
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician (retired) Nov 11, 2022 #3 It also needs to be marked to indicate the location of the disconnecting means.
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Nov 11, 2022 #4 There is no restriction on the length of the conductors that supply the transformer, but 240.21(C) puts length restrictions on the conductors that are supplied by the transformer.