Been doing a lot of temporary transformers lately; they're all used; in the neighborhood of 112kVA. Where in the world do I find the torque requirements for the transformer lugs??
This is the first time I've done any transformers and I can't find the torque values on any of the labels or stamped into the lugs or anything. I'm not real comfortable just doing it by hand until it the metal squeaks, especially with aluminum....
-John
Or from the NECHB.
Commentary Table 110.3 Torques for Recessed Allen Head Screws
Socket Size Across Flats (in.) Torque (lb-in.)
1/8....................................................... 45
5/32.................................................... 100
3/16.................................................... 120
7/32.................................................... 150
1/4...................................................... 200
5/16.................................................... 275
3/8...................................................... 375
1/2...................................................... 500
9/16..................................................... 600
EDIT: Poor computer skills
Thanks for the replies. Going online and getting the paper work seems like the best option when available.
How universal are those torque values from the handbook?
For the transformers I've done so far, I ended up getting the values off of similarly sized lugs and using those. The 5/16 hex were in fact 275 in./lbs. But I noticed that on breakers, the same size lugs might be 350 in./lbs. or more, so I wasn't too sure which number to pick....
-John
What the NECH commentary says -
Section 110.3(B) applies where terminations and equipment with tightening torques.
For the testing of wire connectors, for which the manufacturer has not assigned another value appropriate for the design. commentary Tables 1.2 through 1.5 provide data on the tightening torques that Underwriters Labratories uses. these tables should for guidance only if no tightening information on a specific wire connector is available. They should not be used to replace the manufacturer's instructions, which should always be followed.
That is the verbage from the 05 edition.
Electrical torque values are based on the size and material of the screw/bolt and the material being connector, therefore they are "universal".
However the torque value for the lug-to-transformer connection is taken from a "bus bar" table which may be a different value than the lug-to-conductor one.
I think I'll be printing out a copy of that torque list to tape into my Ugly's book. It seems to match what I've been seeing in the field.
Thanks for the help, and happy Turkey Day!
-John
Or from the NECHB.