kingpb said:
You do have to make sure that the THHN you are using is rated for 90 deg C in wet or dry locations.
Some THHN, including multiconductor may ony be rated ror 75 deg C in wet locations. (i.e. UG)[/quote]
Take a look at the 90C column in Table 310.16 (conductor Types)
Also take a look at 310.8(B) &(C) - THHN is not permitted in wet locations.
You may be thinking of todays conductors with the Copolymers that are dual rated as THHN/THWN, where the THHN part is 90C in dry locations and the THWN is 75C in wet locations.
Actually, no I wasn't:
"Southwire's Type TC Power Cable is used to supply power to motors, or for connection to other power devices in industrial settings. Primary installations include cable trays, raceways, and outdoor locations where supported by a messenger wire. Type TC Power Cable is listed for direct burial and for use in Class 1, Division 2 hazardous locations and Class 1 control circuits. This cable may be used at temperatures not to exceed 75?C in wet locations and 90?C in dry locations. 6 and 8 AWG constructions with insulated grounds (standard) and 4 AWG and larger with bare or insulated ground are UL Listed for exposed runs (ER) per NEC 336.10."
Also, I think you may have forgotten about 310.8(C)(3) since the cable in reference is listed for wet locations, and it does have a PVC (THHN) insulation.
http://appprod.southwire.com/ProductCatalog/XTEInterfaceServlet?contentKey=prodcatsheet67