XHHW underground

Status
Not open for further replies.

Juanvaldez

Member
Location
Ohio
is this an accaptable installation? 4" sch 40 PVC, 3-750 al XHHW run in conduit to a transformer (45'). Conduits terminate at edge utility co transformer. Conduits do not 90 up into transformer, but stop at edge. Is XHHW permitted to be ran this last 24" into transfrormer, W/O continous run of PVC?
 
are they buried in the dirt or is there a cavity under the pad ?
 
are they buried in the dirt or is there a cavity under the pad ?
Sounds like they didn't stub up from 24" down and came straight up with the conductors. Is it USE cable? If it is just xhhw I think it needs to be in conduit.
 
Last edited:
What if it is in a open cavity under the slab in free air and not buried under/in dirt ?
 
Do the 4" PVC conduits run into a box out under the pad? If so then I would say you are ok, otherwise you should have the conduits turned up into and above the pad.
 