XHHW

Status
Not open for further replies.

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Good question. How could they do that.... They would have to exempt it under many conditions except when temps got above whatever it is that the insulation is rated for.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
agree,,, just surpriosed that has not come up at the CMP meetings.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Currently there is no exception for XHHW in attics so the normal ampacity adjustments are required.
 