naplespete57
Member
- Location
- Eastern Kentucky
- Occupation
- Project Manager in Conveyor Industry
Is it always required to tie the XO terminal in a Transformer to building steel or is it simply common practice?
And is often the simplest solution but keep in mind the building steel is not the GE. It is the bonding conductor to the GE. So the building steel has to be bonded to a qualified GE.There are a few exceptions (See 250.30) but many transformers require a grounding electrode on the secondary. Building steel often meets the requirement.
Even if the steel is not bonded to a qualified grounding electrode, 250.140(D)(2) will require the grounded conductor of a separately derived system to be bonded to the steel.And is often the simplest solution but keep in mind the building steel is not the GE. It is the bonding conductor to the GE. So the building steel has to be bonded to a qualified GE.
This subject is what I also had a question on. According to NEC every building or structure supplied by a feeder except multi wire branch circuit exception must connect to a grounding electrode systemThere are a few exceptions (See 250.30) but many transformers require a grounding electrode on the secondary. Building steel often meets the requirement.
Boss tripped out today not because the electrical system wasn’t working (which it was) but because the EMT and round box was supported to the metal shed roof.You would need to meet both requirements. You can use the same grounding electrode system for the feeder and the transformer secondary.
It's no different from your having a service to a large building with a SDS transformer inside.