I have Process Skid to be wired. It is going in a Class I Division 2 area. All instruments & devices (mostly 4-20ma loop devices) on it, except one, are rated Non-Incendive. I'll have a NEMA 4X junction box with only terminals in it where everything is wired back to. Wiring from the JB to off the skid, to the customers non-classified control room, is the customer's responsibility.
The one device that is not N.I. is listed for Class I Division 1, XP or Intrinsically Safe wiring. It is a loop powered (4-20ma) pressure transmitter. I don't want to do I.S. as I would need to have a separate unique conduit from it to the JB, separated wires in the JB and then another unique conduit into the safe are where the I.S. barrier (or isolator) is.
If it were a C1D1 area, I know for XP wiring I would need a seal-off at the device and all fitting / flex must be listed for C1D1.
But it's a C1D2 area. While I know (?) that a seal-off is needed at the device, what about after that to the JB and then control room? Do I need to do the whole run XP and not enter the JB that has terminals for the N.I. items?
Or do I just put a seal-off going into the JB (from the conduit to the XP device)?
Do I need XP listed fittings / flex after the device seal-off ?
The one device that is not N.I. is listed for Class I Division 1, XP or Intrinsically Safe wiring. It is a loop powered (4-20ma) pressure transmitter. I don't want to do I.S. as I would need to have a separate unique conduit from it to the JB, separated wires in the JB and then another unique conduit into the safe are where the I.S. barrier (or isolator) is.
If it were a C1D1 area, I know for XP wiring I would need a seal-off at the device and all fitting / flex must be listed for C1D1.
But it's a C1D2 area. While I know (?) that a seal-off is needed at the device, what about after that to the JB and then control room? Do I need to do the whole run XP and not enter the JB that has terminals for the N.I. items?
Or do I just put a seal-off going into the JB (from the conduit to the XP device)?
Do I need XP listed fittings / flex after the device seal-off ?