When doing infinite bus method calculation engineer gave me percent x/r ratio instead of transformer impedance %z. He then did the following:
(Xfmr kva)/(kv voltage* x/r ratio*-.732)= infinite xfmr short circuit fault current at xfmr secondary
Can one use percent x/r ratio when doing infinite bus method? Is percent x/r same as %z?
(Xfmr kva)/(kv voltage* x/r ratio*-.732)= infinite xfmr short circuit fault current at xfmr secondary