Hi guys,
I'm working on a project with an Xray machine involved. I haven't really dealt with these before, but from what the sales guy says, the main panel for the x-ray room only accepts 480V, 3 phase, and has a 60amp breaker on it. the x-ray machine itself is rated at 65kW / 99kVA.
I'm assuming since the breaker is 60amps, that 99kva is the momentary rating since 50% of that is right under 60 amps.
The building only has 120/208V, 3 phase available, so the sales guys says we'd need a transformer to step up the voltage. Since the main panel for the x-ray room is only 60amps, should i size the transformer according to the 60 amps (about 50kva) or the 99kVA rating of the xray machine?
The only code I could find mentions the branch circuit and over current protection device, which technically shouldn't apply to me since we're only providing power to their panel. So the branch circuit and ocpd of the xray itself is not really in our scope.
Thanks for any input guys!
I'm working on a project with an Xray machine involved. I haven't really dealt with these before, but from what the sales guy says, the main panel for the x-ray room only accepts 480V, 3 phase, and has a 60amp breaker on it. the x-ray machine itself is rated at 65kW / 99kVA.
I'm assuming since the breaker is 60amps, that 99kva is the momentary rating since 50% of that is right under 60 amps.
The building only has 120/208V, 3 phase available, so the sales guys says we'd need a transformer to step up the voltage. Since the main panel for the x-ray room is only 60amps, should i size the transformer according to the 60 amps (about 50kva) or the 99kVA rating of the xray machine?
The only code I could find mentions the branch circuit and over current protection device, which technically shouldn't apply to me since we're only providing power to their panel. So the branch circuit and ocpd of the xray itself is not really in our scope.
Thanks for any input guys!