I ran across a Y-Delta starter that fused together and would not release on stop signal. Looking into the cause, i would say the springs inside the contactor are weak and need replacing.
The question i have is on the size of the M 1 and M 2 contactors for the Y-start and Delta run. Each is rated at 500 HP and 580 amps. The motor is for a chiller and the HP rating is 1171 and the FLA is 1319. Is this normal, or does M1 and M2 stay energized in the run position carrying half the load each? The unit has over 400 starts on it and is about 8 years old.
Rick
The question i have is on the size of the M 1 and M 2 contactors for the Y-start and Delta run. Each is rated at 500 HP and 580 amps. The motor is for a chiller and the HP rating is 1171 and the FLA is 1319. Is this normal, or does M1 and M2 stay energized in the run position carrying half the load each? The unit has over 400 starts on it and is about 8 years old.