We are doing an installation in the
Caribbean where we are creating our
power and distribution. We have
parallel generators that are non
separate derivate system (neutral is
floating in the generator) serving a
parallel generator switchgear. The
voltage generated is 277/480V-3PH-4W.
Each generator is protected with
electronic circuit breakers.
The generator switchgear neutral bar
and ground bar are bonded together.
From the generator switchgear, a
branch electronic circuit breaker is
serving 3000 KVA wye-wye transformer
with 3PH-4W 277/480V primary and
12,470/7200 3PH-4W secondary . The
primary 480V feeder from the branch
breaker to the 3000 KVA transformer is
5W(a,b,c,n and eq ground).
The power distribution to each group
of houses is at 12470/7200V-3PH-from
the secondary side of the 3000 KVA
transformer.
We found out that the neutral
conductor of the primary
feeder(480V)is bonded at the primary
side of the 3000 KVA transformer,and
the secondary feeder(12,470V)is bonded
at the secondary side.
My problem is that the switchgear
branch breaker serving the 3000 KVA
transformer is tripping.
I believe that the primary neutral
bonding should be deleted;this neutral
should be floating, not bonded and the
secondary neutral bonding should
remain. In this way the breaker will
not trip.
Please,fellas, let me know if I am
correct
Caribbean where we are creating our
power and distribution. We have
parallel generators that are non
separate derivate system (neutral is
floating in the generator) serving a
parallel generator switchgear. The
voltage generated is 277/480V-3PH-4W.
Each generator is protected with
electronic circuit breakers.
The generator switchgear neutral bar
and ground bar are bonded together.
From the generator switchgear, a
branch electronic circuit breaker is
serving 3000 KVA wye-wye transformer
with 3PH-4W 277/480V primary and
12,470/7200 3PH-4W secondary . The
primary 480V feeder from the branch
breaker to the 3000 KVA transformer is
5W(a,b,c,n and eq ground).
The power distribution to each group
of houses is at 12470/7200V-3PH-from
the secondary side of the 3000 KVA
transformer.
We found out that the neutral
conductor of the primary
feeder(480V)is bonded at the primary
side of the 3000 KVA transformer,and
the secondary feeder(12,470V)is bonded
at the secondary side.
My problem is that the switchgear
branch breaker serving the 3000 KVA
transformer is tripping.
I believe that the primary neutral
bonding should be deleted;this neutral
should be floating, not bonded and the
secondary neutral bonding should
remain. In this way the breaker will
not trip.
Please,fellas, let me know if I am
correct