hmspe
Senior Member
- Location
- Temple, TX
- Occupation
- PE
A colleague has several new PV sites where the PV inverters are at 480V but the service is 208V. The step-down transformers are 30KVA and the utility has required that they be Y-Y. The PV system uses the neutral on the 480V side for monitoring only, but a neutral connection is required.
The neutral current on the 208V side is unusually high and the phase currents are badly imbalanced if the neutral on the 208V (utility) side is connected. The currents are balanced if the 208V side neutral is lifted, but the utility requires the neutral be connected. The 208V side has neutral and ground bonded by the MBJ in the electrical service. On the 480V side neutral and ground are bonded in the transformer. The representatives from the transformer manufacture who have been to the site say that it's a third harmonic problem that the utility needs to fix. The utility representatives say there's a problem with the transformers.
One test that was run had all building loads disconnected in the electrical service and had the PV system disconnect on the 480V side of the Y-Y transformer open, so the Y-Y transformer wan the only load being served by the electrical service and the transformer had no load connected. Phase loads measured at the transformer were balanced at about 21 amps and the neutral was about 63 amps. That seems really high for magnetizing current for an unloaded transformer.
Not finding much on the internet other than that Y-Y at this voltage level is not generally considered a good idea. Any help or suggestions on what may be causing the current imbalances and/or how to set up the grounding an bonding to make this work would be appreciated.
The neutral current on the 208V side is unusually high and the phase currents are badly imbalanced if the neutral on the 208V (utility) side is connected. The currents are balanced if the 208V side neutral is lifted, but the utility requires the neutral be connected. The 208V side has neutral and ground bonded by the MBJ in the electrical service. On the 480V side neutral and ground are bonded in the transformer. The representatives from the transformer manufacture who have been to the site say that it's a third harmonic problem that the utility needs to fix. The utility representatives say there's a problem with the transformers.
One test that was run had all building loads disconnected in the electrical service and had the PV system disconnect on the 480V side of the Y-Y transformer open, so the Y-Y transformer wan the only load being served by the electrical service and the transformer had no load connected. Phase loads measured at the transformer were balanced at about 21 amps and the neutral was about 63 amps. That seems really high for magnetizing current for an unloaded transformer.
Not finding much on the internet other than that Y-Y at this voltage level is not generally considered a good idea. Any help or suggestions on what may be causing the current imbalances and/or how to set up the grounding an bonding to make this work would be appreciated.