darkenergy
- Weirton WV 26062
- semi-retired electrician
As briefly as possible, (for me, you may reply to any degree/length you see fit
) based on the 2021 NFPA 54 (National fuel gas code) and the NEC 2017.
In your opinion, is it code compliant/non-code compliant to bond a gas line (propane or natural) by way of an approved pipe clamp in series (one continuous wire sized for 250.66 based on the largest service entrance conductor) to the GEC ( Grounding Electrode Conductor) on the way to the Grounding electrode?
As stated previously, I found a 'FACT SHEET'; rev.9-06-17 from the AGA (American gas Association), that seems to require… "A direct bond consists of the listed grounding clamp and separate conductor run from the gas piping to the grounding electrode system. Options include: electrical service enclosure, or grounded conductor at electrical service, or grounding electrode conductor, or any installed grounding electrode."
I can find no such requirement for a 'separate conductor' in the National fuel gas code mentioned. Section 7.12 through 7.12.5 Nor 'Annex A' of same, although A.7.12.5 in the Annex seemingly directly contradicts NEC 2017 250.52 (8) (B) not permitted for use as grounding electrodes, ( 3) metal underground gas piping systems. the Annex item specifically names underground in reference to lightning protection systems… Maybe the additional hundred dollars I just spent to have access to NFPA LINK in addition to the annual $175 NFPA dues will provide some answers… After I figure out how to work it.