Absolutely correct on all counts.Sorry, just to make sure "I'm" good. The pic below is compliant? (also, the existing sub could be moved (to the right) to even space BUT doesn't "need" to be?)
Technically the two panels would need to be the same depth when mounted next to each other.
As far as I'm concerned, that 1/8" is insignificant.I'm not reading (or am missing) that interpretation, could you expand? Is there a tolerance? One panel is 3.875" and the other 3.75"...
Say your two panels are different depths (a non-negligible amount). Since the 30" width for each panel has to overlap the other panel left-right (given your available space), the panel that sticks out farther would be in the working space of the other panel.Just read & reread 110 and am not seeing the reference to two adjacent "live parts" having to be the same depth?
Do you see a substantive safety difference (between side by side vs vertically stacked) that would explain that limitation in the allowance, or is it just sloppy wording?You cannot use the 6" exception because the panels are side by side.
I think that the wording is correct. If you sandwiched a 14.5" wide panel between two 10" wireways it would be possible to contact the wireway while working in the panel.Do you see a substantive safety difference (between side by side vs vertically stacked) that would explain that limitation in the allowance, or is it just sloppy wording?
Cheers, Wayne
Wouldn't that also apply to, for example, a panel hidden behind a hinged door in a wall, even if the space was as shallow as possible? The door opening would have to be at least 30" wide, too, right?I think that the wording is correct. If you sandwiched a 14.5" wide panel between two 10" wireways it would be possible to contact the wireway while working in the panel.
That's correct, it's something that is often overlooked with those types of installations. For me I would rather be leaning against wood or drywall then a grounded metal object when working in a live panel.Wouldn't that also apply to, for example, a panel hidden behind a hinged door in a wall, even if the space was as shallow as possible? The door opening would have to be at least 30" wide, too, right?
The depth of the working space is a function of the voltage and the surface behind you while you work on the equipment. The reason why this is, is that instinct is to move backward, away from the live circuit if you get shocked, rather than to the side. It is safest if the surface behind you is insulated, and most dangerous if there is other equipment behind you. Electrically inactive metal behind you, like a chain link fence, or the back/sides of other equipment, would be intermediate.Just read & reread 110 and am not seeing the reference to two adjacent "live parts" having to be the same depth?
One thing that did strike me as peculiar was two panels facing each other (condition 3) needed the 3ft spacing but no reference to two panels being perpendicular (like mine) needing that separation (side to side) - just the 3ft in front.
...Working space requirements for two pieces of equipment on perpendicular walls are independent of each other....