I need to pack as many 650kVA 277V LED fixtures as possible using the minimum copper in 1/2" metal conduit.
Has anyone got a better solution than the following.......
Use......
So one can pack 3 x 8 = 24 fixtures on to each 1/2" conduit leaving the panelboard.......
Do you see any code issues??????
Has anyone got a better solution than the following.......
Use......
3 pole 277V 20A common trip breaker
MWBC using one shared neutral
1/2" metallic conduit with 4 #12 AWG wires (3 phases A,B,C and neutral; assume neutral is not a CCC so no derating????)
Metal conduit is the ground conductor
8 650 kVA/277VAC fixtures per phase (650/277 = 2.35A and 20/2.35 = 8.5)
MWBC using one shared neutral
1/2" metallic conduit with 4 #12 AWG wires (3 phases A,B,C and neutral; assume neutral is not a CCC so no derating????)
Metal conduit is the ground conductor
8 650 kVA/277VAC fixtures per phase (650/277 = 2.35A and 20/2.35 = 8.5)
So one can pack 3 x 8 = 24 fixtures on to each 1/2" conduit leaving the panelboard.......
Do you see any code issues??????