There are several transformers in a building I am working on that don't seem to be properly grounded.
In each case, they have installed a primary wire with a ground wire, "properly" sized according to table 250.122 taking into account the primary circuit breaker. (Ooops - common mistake!)
This same ground wire attaches to the case of the transformer, then also attaches to the XO terminal of the secondary.
Of course this violates the code because the primary wire doesn't comply with table 260.66, which would generally require a heavier wire for the secondary of a 480:208 transformer.
Now, in fixing this, we'd like to take a wire complying with 250.66 from the XO terminal to the nearest building steel.
My question is, must the primary ground wire be disconnected from the XO terminal, or is it allowed to remain in place?
In each case, they have installed a primary wire with a ground wire, "properly" sized according to table 250.122 taking into account the primary circuit breaker. (Ooops - common mistake!)
This same ground wire attaches to the case of the transformer, then also attaches to the XO terminal of the secondary.
Of course this violates the code because the primary wire doesn't comply with table 260.66, which would generally require a heavier wire for the secondary of a 480:208 transformer.
Now, in fixing this, we'd like to take a wire complying with 250.66 from the XO terminal to the nearest building steel.
My question is, must the primary ground wire be disconnected from the XO terminal, or is it allowed to remain in place?