I've wired some marinas, and with the shocks and deaths and code changes, I'm wondering about something.
A body of water can be a reasonable parallel path for current back to the PoCo distribution system or to a substation because they both are grounding the neutral to the earth (the substation even more sow than the distribution system).
If I understand the PoCo distribution wiring correctly, the neutral at the primary and the secondary are both grounded and possibly using the same GEC, right/wrong? If right, then a deteriorating primary neutral connection can cause higher resistance parallel paths back to the source (substation) using the earth or ... the water. And since we are working with such high voltages compared to the usage voltages, it doesn't take much of a deterioration to get a couple/three or more volts between the water and the PoCo neutral.
We ground the neutral at the service, which is usually a little bit away from the water. We know the resistance on the connection to ground is not very low, so there could easily be a voltage between the water and the system ground of the marina.
My thoughts are maybe we should be running a GEC to the water itself, but that just brings the water up to the neutral voltage, and if there is a deteriorating primary neutral close by, the water will get even more step voltage around the marina.
So, maybe we should ground the water AND monitor the GEC to the water for current. When there is enough current on that conductor (and I don't know how much that is) an alarm is sounded so it can be investigated.
Your thoughts?
A body of water can be a reasonable parallel path for current back to the PoCo distribution system or to a substation because they both are grounding the neutral to the earth (the substation even more sow than the distribution system).
If I understand the PoCo distribution wiring correctly, the neutral at the primary and the secondary are both grounded and possibly using the same GEC, right/wrong? If right, then a deteriorating primary neutral connection can cause higher resistance parallel paths back to the source (substation) using the earth or ... the water. And since we are working with such high voltages compared to the usage voltages, it doesn't take much of a deterioration to get a couple/three or more volts between the water and the PoCo neutral.
We ground the neutral at the service, which is usually a little bit away from the water. We know the resistance on the connection to ground is not very low, so there could easily be a voltage between the water and the system ground of the marina.
My thoughts are maybe we should be running a GEC to the water itself, but that just brings the water up to the neutral voltage, and if there is a deteriorating primary neutral close by, the water will get even more step voltage around the marina.
So, maybe we should ground the water AND monitor the GEC to the water for current. When there is enough current on that conductor (and I don't know how much that is) an alarm is sounded so it can be investigated.
Your thoughts?